    As ya'll mentioned before, I found that fire ants had shorted out my contactor. It looked fried so I bought another one along with another overload relay.

    It started and ran for a while but I'm pretty sure the overload kicked in.

    From looking at the pictures below, how would I reset the overload once it's kicked out? I'm also going to adjust the overload to around 50 amps.

    This is the old unit, but it's identical to the new one.




    Last edited by Catdaddy; 11-19-2014 at 09:21 AM.

  2. #2
    Join Date
    Dec 2008
    Location
    Middle of the state
    Posts
    1,436

    Default

    What hp is the pump motor?

  3. #3
    Join Date
    Jan 2003
    Location
    SC
    Posts
    24,466

    Default

    10 hp

  4. #4
    Join Date
    Dec 2008
    Location
    Middle of the state
    Posts
    1,436

    Default

    At 240V (3-phase), you are looking at running load current of 28A. I would expect the overload would be set around 45A.

  5. #5
    Join Date
    Jan 2003
    Location
    SC
    Posts
    24,466

    Default

    It's wired single phase and the relay was set at 46 amps. The new relay is tripping at 46 amps.


    The white button in the middle is a trip indicator and the blue button is the reset. My question is....how do I reset it?

  6. #6
    Join Date
    Nov 2010
    Posts
    1,263

    Default

    Should be able to push the little white button inside the blue block. You may have to wait a little bit after it trips and hit the button for it to reset. Assuming they are thermal overloads, they will have to cool down before you can reset them.

  7. #7
    Join Date
    Dec 2008
    Location
    Middle of the state
    Posts
    1,436

    Default

    Single phase puts you at 50A (running load)

  8. #8
    Join Date
    Jan 2003
    Location
    SC
    Posts
    24,466

    Default

    Quote Originally Posted by SCSportsman View Post
    Single phase puts you at 50A (running load)

    So I should have it set at 50 amps?

  9. #9
    Join Date
    Dec 2008
    Location
    Middle of the state
    Posts
    1,436

    Default

    Probably closer to 75A

  10. #10
    Join Date
    Dec 2004
    Location
    Horry County
    Posts
    3,813

    Default

    The white button inside the blue button, that looks like a phillips head screw, should have two settings manual and auto. Rotate it to manual. Push to reset. If it clicks it was tripped.

    If the overload relay is solid state with phase loss protection you will have to run a jumper through whatever phase you are not using. Since it ran for a while, I doubt that is the case.


    OL relay needs to be set at 60A (FLA + 20%). If it continues to trip after setting to correct trip point, you need to check the amps while it is under a load.

  11. #11
    Join Date
    Dec 2008
    Location
    Middle of the state
    Posts
    1,436

    Default

    Quote Originally Posted by FLS View Post
    The white button inside the blue button, that looks like a phillips head screw, should have two settings manual and auto. Rotate it to manual. Push to reset. If it clicks it was tripped.

    If the overload relay is solid state with phase loss protection you will have to run a jumper through whatever phase you are not using. Since it ran for a while, I doubt that is the case.


    OL relay needs to be set at 60A (FLA + 20%). If it continues to trip after setting to correct trip point, you need to check the amps while it is under a load.
    Actually, what he said. Not sure why I put 75A, shouldn't type and talk on the phone at the same time. For a 1.15 service factor motor it would be 1.25 x RLA or 62.5A.

  12. #12
    Join Date
    Jan 2003
    Location
    SC
    Posts
    24,466

    Default

    Quote Originally Posted by SCSportsman View Post
    Actually, what he said. Not sure why I put 75A, shouldn't type and talk on the phone at the same time. For a 1.15 service factor motor it would be 1.25 x RLA or 62.5A.

    This relay adjusts up to 63 amps.


    Thanks guys.

  13. #13
    Join Date
    Jan 2003
    Location
    SC
    Posts
    24,466

    Default

    I give up. Couldn't get it to reset. I've wasted 5 days on this mess.

    Looks like I'll just start hunting in Arkansas after Christmas.


    Here's what it looked like for 30 minutes.


  14. #14
    Join Date
    Dec 2004
    Location
    Horry County
    Posts
    3,813

    Default

    Give the relay some time. If it's bimetallic it will take a while to cool off and reset. When it does disconnect motor leads from the bottom of the OL relay and turn it on. If it closes and stays closed your motor is the problem. FWIW single phase motors suck. Internal switches and capacitors are good for my business though.
    You might want to look at using a Variable Frequency Drive to go from single to three phase, allowing you to use a 3 phase motor which will cost about half what single phase will. The initial cost of the drive will be recouped through increased motor longevity and decreased repair costs. They have gotten significantly less expensive and more user friendly in the past 10 years. You can also fine tune the motor speed to prevent cavitation and impeller wear.

  15. #15
    Join Date
    Jan 2006
    Location
    Anderson
    Posts
    2,399

    Default

    Do you mean a phase converter or are you saying get three phase power from a VFD?
    \"Go to Know\"

  16. #16
    Join Date
    Dec 2004
    Location
    Horry County
    Posts
    3,813

    Default

    Not a phase converter, a VFD. Yes single phase in, three phase out. Supply has to be 220v and it approximately doubles the size of the drive(amps). 10 hp motor would take a 20 hp drive. You have to disable the incoming phase loss protection.